pvr said:
I could - but power cuts are not always scheduled
Hi Paul,
This is my specialist subject!
You can if you so wish bak feed your home distribution board through a spare outgoing way! you can connect the generator supply to the outgoing way but keep the outgoing way OPEN.
The the power cut occurs, turn off the main incomer to the dist board (creating your own power cut and isolation) then load shed the items that you do not want to power and start the generator, allow it to stabilise and then close the outgoing way that you have already connected to.
when the power returns, because you have the main incomer open (this was opened by you on the onset of the power cut) you will be able to determine when the change back to normal services occurs.
shut down the sensitive stuff that is being run by the generator, open the generator incoming supply to the distribution board (the one you had connected to previously) and then when safe, close the original incomer. (back to normal).
Don't forget that the generator needs an independent earth.
dont forget to have sufficient fuel available (size of the fuel tank should be a consideration to prevent having to fill the tank whilst in service.
when sizing the size of the generator required, make sure that you compensate of any "on line" UPS systems that may be in use.
if you need more advise in the area, i'm happy to help
Dario