chris6 said:Tim
The condensate pipe can be pumped if no alternative . Tank & pump installed with a switch to control pump when condensate reaches a set level.If passing through loft pipe should be well insulated to avoid freezing. Termination of condensate pipe must meet regs as per normal.
Chris
Great, thanks Chris thats really what I wanted to know and if possible to do as an alternative to relocating the boiler which I imagine will be alot more expensive, its something I can suggest to the plumber if he can't route the condensate pipe via the kitchen.
Tim.